Any change that you log your AC voltage that the inverter reports? I’m not to sure but I think I read that error 47 could be related to to high AC voltages. This can happen because of to thin wires (do you use 1.5mm2 or 2.5mm2 for AC wire?) or bad house installation. Or even to much production in the part of your local grid. Another reason could be some problem in your power grid. A short power outage or things like that. |
Beta Was this translation helpful? Give feedback.
-
As an electrician, the 1,5m2 wires ARE OK (1,5mm2 for 13A and 2,5mm2 for 20A). This has nothing to do with the wire size. When you have only one inverter on the line it's ok. The inverters are not aware what the wire size is :) |
Beta Was this translation helpful? Give feedback.
-
This discussion has been automatically locked since there has not been any recent activity after it was closed. Please open a new discussion for related concerns. |
Beta Was this translation helpful? Give feedback.
-
Hi,
during the last days sometimes I notice a yellow bar in my OpenDTU-onBattery-GUI and see inverter "producing off".
Often this occurs when it was put to max limit of 1500W by OpenDTU.
After going off I have to restart the inverter, switching on is not accepted.
Even updating today to version 51a21de didn't help
I have no idea what happens but switched console on because of that behaviour and send a snippet in the attachement.
Can someone find an explanation?
20230611-Konsole.txt
The GUI also often shows error no. 47.
Thanks in advance - Ingo