Power Limiter - strange behaviour? #225
-
Beta Was this translation helpful? Give feedback.
Replies: 4 comments 2 replies
-
First of all, I find the distance between the upper and lower power limit too narrow because when the inverter is switched on, the battery voltage drops. This can be as much as one volt. |
Beta Was this translation helpful? Give feedback.
-
Thanks for the hint on MQTT - i think i understand the system a bit better now. It seems it works too well :) When power consumption reaches 0 on the smartmeter - MQTT seems not to broadcast any updates any more - which could cause the timeouts. If i manually change power between net-from-grid to net-to-grid I see the following on the console: With power from grid: 12:48:34.262 > RX Channel: 40 --> 95 83 12 22 24 83 12 22 24 81 00 01 00 AA 00 00 03 E8 FF FF FF FF 01 68 00 A2 9F No power from grid (but going to grid): So - no MQTT messages received, MQTT update arrive once every minute --> might be a too long interval for the power limiter? |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
power limiter expects a positive value for power from grid and a negativ value for power to grid. |
Beta Was this translation helpful? Give feedback.
power limiter expects a positive value for power from grid and a negativ value for power to grid.
So why don't you send on one topic
"power from grid" - "power to grid"
, or on 2 different topics "power from grid" and on the second topic "power to grid * -1"